Steady state current waveform are shown in Figure 55 and Figure 56 for different load conditions 612 W and 1364 W, respectively.

Figure 55. Steady State 208-Vac IN, 600-V DC OUT 612W, iTHD 2.5%TIDM-1000 SteadyState_208_612W.png
Figure 56. Steady State 208-Vac, IN 600-V DC OUT 1364W, iTHD 0.96%TIDM-1000 SteadyState_208_1364W.png

Table 4 lists the detailed test results of this design below varying load conditions with 208-Vac input and 600-V DC output.

Table 4. Detailed Test Results With 208Vac IN, 600V DC OUT, and Varying Power Levels

Vbus_PM Vbus_MN VoutTotal PIN Iout Pout Eff THD% PF
297.85 300.5 598.35 74 0.117 70.00695 0.946039865 23.20% 0.8263
298.58 300 598.58 124.4 0.2 119.716 0.962347267 17% 0.9206
299.12 299.8 598.92 245.1 0.4 239.568 0.977429621 8.09% 0.9777
299.78 299 598.78 481.3 0.788 471.83864 0.980342074 3% 0.994
299.52 299.6 599.12 623.7 1.022 612.30064 0.981723008 2.54% 0.9964
299.66 299.4 599.06 858.8 1.405 841.6793 0.980064392 1.71% 0.998
299.84 299.1 598.94 1001.6 1.637 980.46478 0.978898542 1.52% 0.9984
299.3 299.82 599.12 1150.6 1.878 1125.14736 0.977878811 1.22% 0.9988
300.13 298.8 598.93 1399.7 2.278 1364.36254 0.974753547 0.96% 0.999

Figure 57 shows the efficiency data plotted below these test conditions.

Figure 57. Efficiency at 208-Vac IN and 600-V DC OUTTIDM-1000 D001_TIDUCJ0.gif

Figure 58 shows the THD data plotted below these test conditions.

Figure 58. THD at 208-Vac IN and 600-V DC OUTTIDM-1000 D007_TIDUCJ0.gif

Figure 59 shows the PF data plotted below these test conditions.

Figure 59. PF at 208-Vac IN and 600-V DC OUTTIDM-1000 D005_TIDUCJ0.gif

Figure 60 shows the power analyzer capture of the harmonics of the current when operating at 208Vrms input, 600V DC output and 1.2kW load.

Figure 60. Power Analyzer Capture of Harmonics at 208-V AC Input, 600-V DC Output, 1.2-kW LoadTIDM-1000 tidm-1000-poweranalyzer-image.jpg